@hish747
If it helps, the comparison that I usually make to explain voltage and current (and power) is with water pipes.
Imagine that voltage is pressure of the water and current is size/diameter of the pipe, while power is flow.
If you have a very small pipe with a very high pressure in it, or a large pipe with a lower pressure, you may have the same flow.
The fundamental equation is V x A = W i.e. voltage, expressed in Volts, multiplied by current, expressed in Amperes, equals the power, expressed in Watts.
Not unlike water, electricity can be delivered at relatively high voltage (pressure) in small wires (pipes) or at relatively low voltage in large wires.
There is a lot of confusion with PoE, which is a complex standard that many manufacturers (including Mikrotik) have often implemented in different ways, creating BTW the "non-standard" Passive PoE that can be anything and the contrary of it.
The PoE and PoE plus standards, respectively 802.3af and 802.3at:
https://en.wikipedia.org/wiki/Power_ove ... ementation
use anyway voltages between 42 and 57 V, because the wires the electircity is transmitted on (your normal Cat 5 or greater network cables) are tiny so a relatively high voltage is needed to deliver the needed power.
The 802.3af is limited to lower power devices.
What you need/will be using is the 802.3at.
It is limited by the standard at a power at the PD (Powered Device) of 25.5 W.
Mikrotik put a limit to the amount of current each port can deliver at 450 mA (or 0.45 A) on a single port when using the (higher) voltage the PoE 802.3at demands.
So, to draw the maximum power allowed you need 25.5 W / 0.45 A= 56,67 V.
If we take (as an example) a Zixel AX 3000:
https://www.zyxel.com/global/en/product ... ifications
it needs 20.5 W.
20.5 W / 0.45 A = 45,55 V
Since a few Volts will likely be "lost" in the length of cable between the PoE router/switch and the AP 48 Volts is the minimum you can expect the AP to work with.
The "size" of the PSE (Power Sourcing Equipment) depends on how many devices you are going to power.
The hEX PoE can consume up to 54 W per specifications, so if you have only one AP connected to it your power supply should be capable of powering 54+20.5=74.5 W (very likely the hex Poe will need much less than that in normal operation, still ... )
If the voltage is 48 V, you need 74.5 W / 48 V = 1.55 A, in practice you need a 48 V / 2A power supply, or more likely you will find 80 W PoE injectors that are 54 or 56 V (54 V x 1.5 A = 81W, 56 V x 1.45 A = 81,2 W), example:
https://en.cdr.pl/p5249,ubiquiti-gigabi ... v-80w.html
The power supply that you got togeher with your hex Poe is a 24V 2.5A one and - besides the fact that voltage is not 802.3at compatible - it can only power the hex as 24 V x 2.5 A = 60 W, very similar to the max power of 54 W in specifications.