I’m running two 500’s on a remote battery/solar set-up.
There are two 125 a/hr deep-cycle batteries charged from a 160w solar array and so far the batteries have been keep pretty much at full-charge through one winter.
Currently (!) the batteries are hooked up in parallel, delivering around 13 volts but with a notional 250 A/hr but we have the option of hooking them in series delivering 26v to the boards rather than the 13v they get now, and the consensus of these boards seems to be that 12 -13v is low for the 500 which has to up the amps to compensate.
However the 500 set-up guide gives the JP3/JP4 positions as 1-2 for 25-56v and 2-3 for 6 - 24v. With the batteries in series a prolonged run of sunless weather could take the batteries down to 24v or even less, which is the cusp of the jumper positions. Set the jumpers to 25-56v and you risk underrunning the minimum supply but set them to 6 -24v and you’re going to be a couple of volts over most of the time.