The Battery Charging strategy goes like this :-
If the battery is > 13.8 volts, it leaves it alone, and doesn’t charge it at all.
If < 12.5 volts, it trickle charges it (150mA) back up to 13.8 volts.
If < 12 volts, it fast charges at up to 1.5A until the battery is 13.8v again.
OF COURSE, it will not be charging the battery at all unless there is enoug Solar Power to be running the AP, and extra is left over to charge the battery.
Better to let the battery die than the AP.
So, when the AP is running on Solar Power, (i.e. using nothing from the battery) and there is spare energy from the Solar Panels, the circuit charges the battery.
If there is enough power, and the battery is ‘flat’, as in below 12volts, the circuit will Bulk Charge the battery at about 1.5A, until the battery reaches it’s Maximum charge level.
There are timers to limit how long this can happen, in case the battery cannot accept the charge.
If the battery is partly charged, i.e. above 12v, then it will get a Maintenence charge of about 150~200mA until it reaches the Full level.
If the Battery is above 12.5v then it is not charged at all, but is allowed to gradually reduce to the 12.5v level.
Maybe i have not got the trigger voltages right yet, but it seems to work pretty well.
If there are any Lead Acid Charging experts out there, sound off.