POE-CON-HP with -48Volts

Hello all

We have several sites that run with telecom -48Volts and we want to use POE-CON-HP to generate 24Volts. But are the input and output voltages isolated? Because when using telecom minus 48Volts as an input, the positive connection is the ground and the negative is the -48Volts. And that might be correct but a bit irregular. Is the output voltage floating or isolated from the input voltage?

Has anybody ever used it with telecom -48Volts with the positive pin grounded?

Thanks

But are the input and output voltages isolated? Because when using telecom minus 48Volts as an input, the positive connection is the ground and the negative is the -48Volts. And that might be correct but a bit irregular. Is the output voltage floating or isolated from the input voltage?

Yes.

Thanks for the quick reply!

Regards